Cheap Backup Option for running Modem during Powercut?

  • Thread starter Thread starter Shivam15
  • Start date Start date
  • Replies Replies 22
  • Views Views 7,731
Your normal inverter would work. Just get a electrician to wire your socket (near modem) to inverter.

It certainly works, although I wouldn't say it's efficient. But then yeah if you already have a power backup system for your entire house, perhaps it makes sense.

But then if it's specifically for the routers and modems, I would say a DC UPS is way more efficient.
 
do keep posted about the project..
 
@varkey correct me if I am wrong,
I don't think a DC-DC converter would have efficiency greater just based on the fact that it's only DC-DC converter because even a DC-DC converter would first convert the input signal to square/sin wave and then stepup or step down it and then back again to DC which is same as DC --> AC --> DC which would happen on normal UPS configuration
The only difference I think is that there will be 1 less transformer in the circuit and less amount of stepup/down is needed
 
@Rehan Kumar You'd need to step down the voltage only if you need 5V or so. Since most devices these days work with 12V or so you don't even need to do that. So it's just the output from the battery which goes to devices directly when AC input is absent. There is no voltage regulation happening AFAIK. And when running on AC input, it works as a regular power adaptor which outputs DC.

If you do need 5V, wouldn't you still be better off using a buck converter? Rather than make it 220 V AC, then attach the original power adaptor of the device which converts to 5V DC. Maybe I'm wrong here but a buck converter could reach pretty high efficiencies 80-90%?
 
So I went to purchase the battery today and had a good discussion with couple of battery shops and for a UPS kind of use case, all of them suggested to keep the charge current at around 0.1 CA (ie 10% of the battery capacity). It is OK if its charge current is a bit less, it would just take longer to charge, but keeping it above 0.1 CA would reduce the battery life.

Based on that I went ahead and purchased a 18 AH battery, Exide PowerSafe Plus. It cost me Rs 2250 incl GST (and was surprised to learn that GST for batteries is 28 % !! )

Even the warranty card which comes with the battery mentions that the max charge current should be only 0.2 CA ie 3.6 A for an 18 AH battery (would be 1.4 A for a 7 AH, 2.8 A for 12 AH, please note this is the max charge current). With the power supply I have giving 1.5 A, it would take a bit longer to charge probably around 15 hours in case the battery is fully drained.

ub3ipmA.webp


The 18 AH battery uses a nut & bolt type of connector, so I got the necessary cable too from the same shop, costed me Rs 50.
 
Last edited by a moderator:
Do post the performance details of the back up supply developed by you.
 